Arc Fault question

Status
Not open for further replies.

WinZip

Senior Member
210.12 B for a sun room - Is Exception 1 regarding 210.12 ( B )

or FPN NO. 1 - 2 - 3

Or all of the above , running rmc , imc , emt ,ac cable to the first metal outlet box then continue in ac cable or nm if aloud.

Getting to old for all these changes haha
 

ceb58

Senior Member
Location
Raeford, NC
210.12 B for a sun room - Is Exception 1 regarding 210.12 ( B )

or FPN NO. 1 - 2 - 3

Or all of the above , running rmc , imc , emt ,ac cable to the first metal outlet box then continue in ac cable or nm if aloud.

Getting to old for all these changes haha

Excpt. 1 is in regard to 210.12 B However it is in regard to using an AFCI recp. as the first devise. At this time no one is selling an AFCI recp.
IMHO the trouble of running ac cable or conduit is not worth the time or effort. Just run nm and install the breaker.
 

WinZip

Senior Member
D U H , I miss read the article ,the way I was reading it service to the first outlet had to be one of the raceways mentioned AC cable etc. then continue on with what ever is aloud from that point.

Sorry for a dumb question
 

ceb58

Senior Member
Location
Raeford, NC
D U H , I miss read the article ,the way I was reading it service to the first outlet had to be one of the raceways mentioned AC cable etc. then continue on with what ever is aloud from that point.

Sorry for a dumb question

The only dumb question is the one never ask;)
 