Is it legal to use an arc fault receptacle in a bedroom of a house instead of a arc fault breaker; in other words does the home run have to be arc fault protected
new installation or simple receptacle replacement?Is it legal to use an arc fault receptacle in a bedroom of a house instead of a arc fault breaker; in other words does the home run have to be arc fault protected
It’s a new house that’s been under construction since we were still doing it the old way so all the neutrals are on the neutral bus bar so it would be easier to use the receptacles rather than ohm out every home run to pair the hots and neutrals back upnew installation or simple receptacle replacement?
2002 NEC required AFCI in bedroomsunder construction since we were still doing it the old way
Isnt this wired with cable so all you have to do is disconnect the white wire, trace it back to the cable jacket, and then follow the black wire in that cable to its breaker.It’s a new house that’s been under construction since we were still doing it the old way so all the neutrals are on the neutral bus bar so it would be easier to use the receptacles rather than ohm out every home run to pair the hots and neutrals back up
Here in upstate NY, most inspectors are private third party so really they are the AHJ. Had an inspector for a few years who allowed AFCI at the first outlet, so I did a duplex with that method. These were pass and Seymour brand and they nuisance tripped all the time. Ended up ripping them out.I know of one jurisdiction in south Georgia that is allowing them in new construction, but is requiring it on the first receptacle regardless how far away from the panel, and not in conduit. A friend of mine built a vacation house down there, and wanted me to check out the builders electrician’s work. After not seeing any arc faults in the panel, I noticed what look like GFI’s all over the house. Looked closer, and they were arcfault receptacles.