I also replaced the receptacles to new white tamper resist. so the inspector is using reference to NEC 406.4 (D) (4) for enforcing the Arc Fault requirement.
Well, that makes a big difference. Inspector is correct. Off to AFCI land for you.
Well, that makes a big difference. Inspector is correct. Off to AFCI land for you.
I agree, next time the OP should wait until after the inspection to change a few receptacles. :roll:
:happyyes:
In general, most jurisdictions do not require a permit for simply swapping devices.
Should have made them separate jobs. Too late now.
You are correct but I must say my first response was somewhat tongue in cheek, you should follow the code whether an inspection is required or not.
Here's the problem I have with this and my response is not specifically Code related. When you're replacing or upgrading an electric service I don't understand why an EI would compel you to now provide either AFCI breakers or 2-P breakers for MWBC's. You're replacing like with like. The circuits have been in existence for "X" years and have functioned just fine. The presumption is that the original electrical system was inspected and Code compliant at the time it was installed. You have no idea how the circuits were run, whether they were properly grounded, how the cables were stapled or supported, etc. I think an EI would be opening up a big can of worms by requiring this. Besides, you gave your customer a price to do the work, now you have to go back and ask for more $$. Electrical contracting is competitive enough - why add another layer of ridiculous requirements to get the job ?
Just my 2 cents worth.:roll:
iv. Section 210.12(B), entitled "Branch Circuit Extensions or Modifications - Dwelling Units," is deleted in its entirety.
Aside from us here in NJ, why would changing receptacles require converting the circuit(s) to AFCI ?The arc fault requirement would apply to the circuits where the receptacles were changed not the entire service. In NJ I believe that you're in luck as they have removed this requirement.![]()
Aside from us here in NJ, why would changing receptacles require converting the circuit(s) to AFCI ?
I'm sorry. I guess I missed 406.4(D) due to the fact that I live in NJ and someone at the State level decided a long time ago that this section would present a hardship for many HO's. As such we EC's in NJ do not have to comply with this section. But, stop and think about this for a moment - you're called out on a service call to a house built in the 1950's and for a defective receptacle:
What if the breaker panel is too old to accept AFCI breakers (I can go on and on with a lot of "ifs") ? Am I missing something or mis-interpreting this section ? I understand the need for safety but this section is ridiculous IMHO. Glad I live in NJ (but that could change if someone at the State level decides to accept the 2017 NEC in its entirety):rant:
- If you leave the existing receptacle in place, irrespective of whether it is grounded or not, you do not have to convert the circuit to AFCI
- If you change out the receptacle - now you have to convert the circuit to AFCI
How lucky can you get ? Go out and buy a lottery ticket.IDK. I do not do resi or service work, so I do not face this problem either.
My whole experience with AFCIs is installing two breakers back in 2006. Never touched another and never trouble shooted a problem with them or anything else AFCI related.
I'm sorry. I guess I missed 406.4(D) due to the fact that I live in NJ and someone at the State level decided a long time ago that this section would present a hardship for many HO's. As such we EC's in NJ do not have to comply with this section. But, stop and think about this for a moment - you're called out on a service call to a house built in the 1950's and for a defective receptacle:
What if the breaker panel is too old to accept AFCI breakers (I can go on and on with a lot of "ifs") ? Am I missing something or mis-interpreting this section ? I understand the need for safety but this section is ridiculous IMHO. Glad I live in NJ (but that could change if someone at the State level decides to accept the 2017 NEC in its entirety):rant:
- If you leave the existing receptacle in place, irrespective of whether it is grounded or not, you do not have to convert the circuit to AFCI
- If you change out the receptacle - now you have to convert the circuit to AFCI
How lucky can you get ? Go out and buy a lottery ticket.![]()
It's been nice to be able to go into a supply house and pick up a box of white, self-grounding TR receptacles (costing about $20) and keep them on our trucks for quick service calls and receptacle change-outs. Are we soon going to have to buy a box of AFCI receptacles at our cost of about $250 and keep them on our trucks ?When you replace just install an AFCI receptacle as Jumper stated no need to try and find an AFCI circuit breaker for that FPE panel.![]()
It's been nice to be able to go into a supply house and pick up a box of white, self-grounding TR receptacles (costing about $20) and keep them on our trucks for quick service calls and receptacle change-outs. Are we soon going to have to buy a box of AFCI receptacles at our cost of about $250 and keep them on our trucks ?
I don't see anything good coming out of this Code requirement for EC's other than the possibility of making a few more $$. However, I think there will be more EC's not complying with this Code section if they don't have to get inspected and more HO's doing their own electrical work to save a few $$.
Just my opinion.![]()