I dont think it is a amperage problem.
I have 3 bedrooms in a row, first bedroom has the sub panel box contain 3 arc fault breakers. The middle bedroom is tripping when ever i use a sawzall in it. the other two bedrooms do not. This is new wiring in building, each room on own circuit. in the middle bedroom i checked for any shorts or neutral to ground found none, i changed the receptacles, and replaced all the wiring, still trips while changing was working until the last run, install jumper but still tripped. all switches were removed. Call Eaton they said it sounds like a "sweet spot" in the length of wiring, and to check for am radio stations. the also said use a surge protector. tried a surge protector and that worked. This is a hard sell to a customer when the other 2 rooms work fine. I did try swapping breakers. I am waiting for Bob (Eaton guru) to call me a hopefully get some sort of documentation and and explanation on this.. Has anybody else had this problem?