• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Arc fault

Merry Christmas

Jcamp28

New User
Location
Iowa
Occupation
Electrical
Can someone please help me understand how to do arc fault calculation for a service? Any help would be much appreciated!
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I'm not aware of any such calculation. I imagine you are referencing the Short Circuit Current available and the AIC Ratings of the service equipment.
IF so, the 1st step normally is to obtain the SCA from your power company.
Once you have that the Bussmann FC² app that is available will often assist you thru the steps.

If in fact that is what you are referencing, here is one of many guides available:
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Can someone please help me understand how to do arc fault calculation for a service? Any help would be much appreciated!
Do you mean to find the Arc Flash Incident Energy value?
The most current version of the IEEE formula is not really conducive to hand calculations.
 
Top