arc faults for panel change?

Status
Not open for further replies.

CopperTone

Senior Member
Location
MetroWest, MA
had an inspector tell me today that he wants arc fault breakers installed where required if we change out the main panel in a residential house. we are doing no other work in the house. old FPE panel coming out.

210.12 doesn't say anything about if you change the panel or breaker you must install arc fault breakers - it only addresses changing or extending the existing branch circuit.

Anyone else have a different opinion?
 

JWCELECTRIC

Senior Member
Location
Massachusetts
had an inspector tell me today that he wants arc fault breakers installed where required if we change out the main panel in a residential house. we are doing no other work in the house. old FPE panel coming out.

210.12 doesn't say anything about if you change the panel or breaker you must install arc fault breakers - it only addresses changing or extending the existing branch circuit.

Anyone else have a different opinion?

What Town?
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
It's the NEC not the TEC. N is for "National" Electrical Code not "Town" Electrical Code. Unless there is a specific city code requirement that amends or exceeds an NEC requirement (like in Chicago or NYC) I don't see how an inspector can compel you to replace regular breakers with arc faults. You're also going to run into a problem with MWBC's.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
had an inspector tell me today that he wants arc fault breakers installed where required if we change out the main panel in a residential house. we are doing no other work in the house. old FPE panel coming out.

210.12 doesn't say anything about if you change the panel or breaker you must install arc fault breakers - it only addresses changing or extending the existing branch circuit.

Anyone else have a different opinion?
What he wants is not enforcable.

I don't think 210.12 is the applicable code. It defines what you have to do when you initially build the thing, or do extensive rebuilding. This is more along the lines of a repair.

Would replacing a single CB on a circuit that would now have to be AFCI require the installation of an AFCI? How is replacing the whole panel markedly different?

Are the bathroom circuits on GFCIs? If not, is he making you install GFCI breakers on those circuits?
 