That is not the question you need to ask. Let me rephrase your question:
Is a Fire Station considered a "dwelling unit" per the NEC 100 definition, or would its sleeping areas be considered "guest rooms" or "guest suites" per NEC 210.18, so that the arc fault rules would apply to the facility?
We have debated this question before. I don't recall whether there was a concensus. My answer to the question would be "no."
That is not the question you need to ask. Let me rephrase your question:
Is a Fire Station considered a "dwelling unit" per the NEC 100 definition, or would its sleeping areas be considered "guest rooms" or "guest suites" per NEC 210.18, so that the arc fault rules would apply to the facility?
We have debated this question before. I don't recall whether there was a concensus. My answer to the question would be "no."
No. Take a look at 210.18. It says to treat the one as though it were the other.Is there a difference in the requirements for AFCI in a dwelling and a guest room/ guest suite?
No. Take a look at 210.18. It says to treat the one as though it were the other.
No, I was just channeling my wife, the reference librarian. They get a lot of patrons that ask vague questions, in a sort of dance around the real subject of interest. They often need to "interview" the patron, in order to find out what it is that the person is really trying to find out.. . . perhaps I miss-understood your previous post, in asking the OP to reword the question I interpreted it to meen there was a difference between dwelling unit and guest suite/guest room.