M MichaelJ Member Location Georgia Apr 20, 2010 #1 Are deadicated circuits for dishwasher, ref, clothes washer and microwave required to be arc-fault protected
Are deadicated circuits for dishwasher, ref, clothes washer and microwave required to be arc-fault protected
mcclary's electrical Senior Member Location VA Apr 20, 2010 #2 MichaelJ said: Are deadicated circuits for dishwasher, ref, clothes washer and microwave required to be arc-fault protected Click to expand... depends on what room they're in
MichaelJ said: Are deadicated circuits for dishwasher, ref, clothes washer and microwave required to be arc-fault protected Click to expand... depends on what room they're in
M MichaelJ Member Location Georgia Apr 20, 2010 #3 dishwasher, micro, and ref in kitchen and clothes washer in laundry
mcclary's electrical Senior Member Location VA Apr 20, 2010 #4 MichaelJ said: dishwasher, micro, and ref in kitchen and clothes washer in laundry Click to expand... no, no, no, and under 08' the last is questionable, but I vote no for it also
MichaelJ said: dishwasher, micro, and ref in kitchen and clothes washer in laundry Click to expand... no, no, no, and under 08' the last is questionable, but I vote no for it also
raider1 Senior Member Staff member Location Logan, Utah Apr 20, 2010 #5 I agree with Mcclary's electrical. No AFCI protection is required for outlets in a laundry room or kitchen per the 2008 NEC 210.12. Chris
I agree with Mcclary's electrical. No AFCI protection is required for outlets in a laundry room or kitchen per the 2008 NEC 210.12. Chris