I don't. I have done but a few analyses, but I haven't worn any special PPE during any one of them. :wink: :grin:rnkish said:When performing an arc flash analysis you are required to wear the proper PPE.
rnkish said:Table 130.7(C)(9)(a) is the table i assume you are refering to.
If I remove a cover and the dead front from a 200a 277/480v Panelboad (available fault current supplied by the local utility is 42 KA) to retrieve catalogue numbers and trip settings only off of the breaker labels the way I read the table is a PPE of 1 is required.
I am seeing this in the second section of the table for Panelboards or switchboards Rated >240V and up to 600V.
Why do you think a listing for "Removal of bolted covers (to expose bare, energized parts)" is not listed here as it is in the previous part of the table Panelboards Rated 240V and Below??
Am I reading this correct??
billsnuff said:see other 600V class (277 throught 600) equipment..........I think your answer is there, see note 2*. JMSO
ron said:Let's pretend you used a Category 1 PPE from the table to make your survey, then after calculation, you determine that the incoming service OCPD's had no instantaneous protection, and the short time was dialed to the max, and you find incident energy >40 cal/cm^2 for several downstream pieces of equip.
Ron -ron said:... Another angle is that I've done many calculations, even at 120/208V panelboards, that have very low fault current and took the equivalent of what might be infinity to have the upstream breaker clear, and determined incident energy at 200cal/cm^2. Yikes!
ron said:Let's pretend you used a Category 1 PPE from the table to make your survey, then after calculation, you determine that the incoming service OCPD's had no instantaneous protection, and the short time was dialed to the max, and you find incident energy >40 cal/cm^2 for several downstream pieces of equip.
ron said:The table notes relate to available fault current and clearing time. Until you do the survey, how do you know if you are compliant with the notes.
ron said:The breakers I'm describing have new solid state trip units already, although the instantaneous is off in order to have selectivity.
ron said:It is always a balance between reliability and arc flash reduction, and many critical facilities prefer reliability.
ron said:It is always a balance between reliability and arc flash reduction, and many critical facilities prefer reliability.