This is the most important question to be asking at this stage for your plant, this is where many plants make a critical error if not being specific about the requirements. I have seen many facilities just put out an RFQ for an arc flash analysis, and get some horrible studies from low bidders who have no idea what they are doing, they just plug numbers into a calculator thinking that is all that is required. The result is data and labels that are in some cases too conservative (Putting people in unnecessary PPE) and also in some areas not having the right values, putting people in inadequate PPE (Endangering lives) because they did not look at different operating modes, motor contributions, and worse case Ei's (Which is often at lower arcing currents, not always the highest).
IEEE 1585 has very specific requirements, and I suggest looking at those and including them as part of your RFQ. Also get references and qualifications of the bidders. The most important part of the entire process is the data collection. The data used is the basis of the results, labels, PPE requirements, and your entire safety program, so it better be accurate. The data collection is about half of the labor hours ($$) so some plants save money by doing that themselves using data collection sheets provided by the company doing the study. Also keep in mind the entire study is based off assumptions of times your breakers trip so if you have not done testing (As required by 70E) to verify they trip in thier required bands, the study is worthless.
Here are the basic elements that need to be in your RFQ.
The analysis shall consist of the following:
1. Field data collection by qualified personnel (as defined by NFPA 70E).
2. Data entry and system one-line modeling in commercially available power system software.
3. Model verification.
4. Short Circuit and equipment verification study.
5. Protective device coordination study.
6. Arc flash hazard study.
7. Detailed report and findings of the analysis.
8. Electronic copies of the Project Report and the System Modeling File.
9. Review of a draft copy of the report and presentation of the final copy of the report in person, via teleconference, or via teleconference and web conference.
10. Hard copies of the project report (note all printing, postage, etc.) shall be included in proposed project pricing.
You are required to update the study every 3 years or if any major changes are made to your system, so you may want to include that as part of the RFQ, and be sure to get an electronic file of the study so you can update in the future should the contractor go out of business. ETAP, SKM, and Easypower are the most common programs to use so if you have the files anyone with the software can make changes for you in the future.
I have a sample RFQ you can use but it is too large to be attached, PM me you email address and I can send it to you if you like.