To calculate Arc Flash Short circuit current(Bolted fault current) is used. But the short circuit current that we consider to evaluate MV equipment and LV (Low Voltage) is different based on IEEE. I was wondering if we have the same senerio when we calculate the arc flash results.
The short circuit for LV circuit breaker evaluation is 1/2 cycle symetrical fault current.
The short circuit for MV and HV circuit breaker evaluation is 1-1/2 to 4 cycles symetrical fault current.
The short circuit for LV circuit breaker evaluation is 1/2 cycle symetrical fault current.
The short circuit for MV and HV circuit breaker evaluation is 1-1/2 to 4 cycles symetrical fault current.