So I will replace 2 switchgear heaters in the HV service disconnects.
Skipping the long story, I didn't trust my first engineer's AF study, so asked another to run some quick numbers to see if my worries were justified. This mini-study shows 220 cal/cm2 after (1 of 2) pad mounted transformers (13.2kV:480wye, 2.5MVA). Extreme danger, about 550" for an Arc-Flash Boundary. It is believable to me.
Of course we will do some true calc's this week, but if the secondary is as shown above, what kind of numbers might we be looking at on the HV side, typically, at the disconnects?
The voltage is 13.2Y/7.62KV.
POCO fuses are Kearney T, 100 amps.
The available fault current is 3285 Amps (LLL), 2320 Amps (LG).
I do not know the conductor type/size, but seems to be 1/3 neutral cables. Length is about 80' from pole cutouts to dual switches.
Obviously much more info is needed, these are complex calculations. I'm not looking for official information here, just experienced guesses of incident energy at that point.
Skipping the long story, I didn't trust my first engineer's AF study, so asked another to run some quick numbers to see if my worries were justified. This mini-study shows 220 cal/cm2 after (1 of 2) pad mounted transformers (13.2kV:480wye, 2.5MVA). Extreme danger, about 550" for an Arc-Flash Boundary. It is believable to me.
Of course we will do some true calc's this week, but if the secondary is as shown above, what kind of numbers might we be looking at on the HV side, typically, at the disconnects?
The voltage is 13.2Y/7.62KV.
POCO fuses are Kearney T, 100 amps.
The available fault current is 3285 Amps (LLL), 2320 Amps (LG).
I do not know the conductor type/size, but seems to be 1/3 neutral cables. Length is about 80' from pole cutouts to dual switches.
Obviously much more info is needed, these are complex calculations. I'm not looking for official information here, just experienced guesses of incident energy at that point.