Arc Flash at Service Disconnect

Status
Not open for further replies.

fun ee

Member
Location
Texas
Since the utility would drive the amount of arc flash energy at a service disconnect, are service equipment (panelboard, circuit breaker disconnect) omitted from having the arc flash analysis in it's scope. Do utilities provide fault clearing times?

Thanks Again
 
For some large systems, they will provide you the upstream protection characteristics, but not for smaller systems.

It is not immune, since you may have to replace a fuse or breaker in there someday and the line side will be energized.
 
Since the utility would drive the amount of arc flash energy at a service disconnect, are service equipment (panelboard, circuit breaker disconnect) omitted from having the arc flash analysis in it's scope. Do utilities provide fault clearing times?

Thanks Again

Agree with Ron, you can usually get fault current from them and just use 2 seconds
 