I?ve read some of the articles and was hoping that some of you could shed some light on a disagreement with a co-worker about NFPA 70E. The co-worker was sent to troubleshoot a Bell & Gosset 480 Volt dual condensate motor/pump that was not running. He shut the (2) disconnects, placed the AoH switch to hand and the pumps did not start. He then opened the panel to verify o level voltage with a Fluke meter, upon verifying that no voltage existed he placed a lock on the disconnects. He performed this work with the following PPE; safety glasses, safety shoes, heavy duty pants, and long sleeve Nomex shirt.
It is my interpretation that this is a violation based on the following;
1) Even with the switch off until the voltage is verified you are suppose to
assume that the voltage could be live.
2) The 480V are still present at the top of the disconnect in the
enclosure however not exposed.
3) Opening a door or removing a cover could expose a worker to electrical
hazards.
4) PPE for flash protection must be worn any time you cross the Arc Flash
boundary and "interact" with the equipment, weather the live parts are
exposed or covered.
5) He also violated the Prohibited Approach Boundary with his meter probe
to verify voltage.
6) Limited, Restricted and Prohibited have nothing to do with Arc Flash
these are shock hazard boundaries only.
My colleague contends that he did not violate NFPA 70E because of the following reasons;
1) He is a qualified electrician and holds a E1 license.
2) He is knowledgeable in the construction and operation of the equipment
associated with the work task and he knew that the existing voltage
was not exposed.
3) With the disconnect in the off position there was no potential for Arc Flash.
4) He did not violate Prohibited Approach Boundary~ 1 inch because of
the design of the meter probe is insulated past the required 1 inch.
5) Verifying voltage is not the same as testing for voltage.
6) Because it was not intentional, and he did not knowingly violate the
code.
Could you please provide some clarity to the code issue?
It is my interpretation that this is a violation based on the following;
1) Even with the switch off until the voltage is verified you are suppose to
assume that the voltage could be live.
2) The 480V are still present at the top of the disconnect in the
enclosure however not exposed.
3) Opening a door or removing a cover could expose a worker to electrical
hazards.
4) PPE for flash protection must be worn any time you cross the Arc Flash
boundary and "interact" with the equipment, weather the live parts are
exposed or covered.
5) He also violated the Prohibited Approach Boundary with his meter probe
to verify voltage.
6) Limited, Restricted and Prohibited have nothing to do with Arc Flash
these are shock hazard boundaries only.
My colleague contends that he did not violate NFPA 70E because of the following reasons;
1) He is a qualified electrician and holds a E1 license.
2) He is knowledgeable in the construction and operation of the equipment
associated with the work task and he knew that the existing voltage
was not exposed.
3) With the disconnect in the off position there was no potential for Arc Flash.
4) He did not violate Prohibited Approach Boundary~ 1 inch because of
the design of the meter probe is insulated past the required 1 inch.
5) Verifying voltage is not the same as testing for voltage.
6) Because it was not intentional, and he did not knowingly violate the
code.
Could you please provide some clarity to the code issue?