I recently took an arc flash class they specified that after an arc flash the breaker should be tested what does this test include? What equipment do I need to test breakers?
 

Drake5265

Member
The Facility that I work in uses a testing firm to test the breakers when there is a problem with them. Its usually a bench tester for circuit breakers you can find them at grainger and probably at graybar. Check the manufacturers guidlines on testing the circuit breaker before testing it. To do a quick test you should have a hand tester for this circuit breaker to test the trip unit functionality and the other functions as well.
 

zog

Senior Member
Location
Charlotte, NC
I recently took an arc flash class they specified that after an arc flash the breaker should be tested what does this test include? What equipment do I need to test breakers?

What type of breakers you talking about? Small MCCB's, MV Vacuum breakers? 480V ACB's? Electronic trip or series trip units? All different equipment and test procedures.
 