I need perform arc flash study using SKM. I need to model utility two single phase Delta-Delta transformers; one transformer has 75kVA, Z=1.3%, and the other has 50kVA, Z=1.2%.
These two single phase transformers are configured as open delta configuration to take 3 phase 13.2kV LL and step it down into delta secondary 240/120V
as shown in the
I'm working with SKM to calculate Arc flash IE's on the buses fed off these utility transformers. I need to model everything as 3 phase.
I plan to have two cases;
1- MAX SC - Model a 3-phase (Delta-Delta) 75kVA transformer with its open delta rating of 43.3kva (75x57.7%) and Z=1.3%, with 10% tolerance.
2- MIN SC - Model a 3-phase (Delta-Delta) 50kVA transformer with its open delta rating of 28.9.3kva (50x57.7%) and Z=1.2%, with 10% tolerance.
Am I on the right track to end up with conservative Arc flash results? Any other suggestion? Thanks in advance for your help.