B Barry1 Member Mar 20, 2012 #1 Did the new 2012 70E standard do away with the 130.3 exception no. 1: an arc flash analysis shll not be required where all of the followingconditions are met: 1. 240v or less 2. one x-former 3. x-former rated less then 125kva
zog Senior Member Location Charlotte, NC Mar 20, 2012 #2 Yes and no, they removed the verbage but refered you to the IEEE 1584 article that says the same thing.
J jdhaze Member Location Birmingham, AL Apr 17, 2012 #3 zog said: Yes and no, they removed the verbage but refered you to the IEEE 1584 article that says the same thing. Click to expand... Can you list for me with the section/subsection number you are quoting this from?