Hello,
I was wondering what your take is on arc flash hazard calculations for sectionalized, low voltage switchgear and switchboards which are not arc-resistant rated. My philosophy has always been to apply a label representing the worst case incident energy at the line side of the main circuit breaker to all sections of the gear.
Is it acceptable in your opinion to apply a separate label at the main (representing incident energy at the line side of the main), and then a separate label to the non-main sections (representing incident energy at the load side of the main) even if the gear is not arc-resistant rated?
If you're looking for an example equipment type/mfg. think Schneider PZ4 or QED-2.
Let's discuss.
I was wondering what your take is on arc flash hazard calculations for sectionalized, low voltage switchgear and switchboards which are not arc-resistant rated. My philosophy has always been to apply a label representing the worst case incident energy at the line side of the main circuit breaker to all sections of the gear.