I need help understanding Nfpa 70e table 130.7(c)15(a)
Which states
“ panel boards, or other equipment rated 240 V and below
Parameters maximum of 25KA available fault current; maximum of 0.03 seconds (2cycles) fault clearing time; minimum working distance, 455 mm (18”)
Arc flash PPE category one”
What I’m failing to find is any information regarding single phase and am interpreting this as, since I don’t know how to calculate the available fault current I’m supposed to get an incident energy analysis, but as far as I know, there is no calculation for single phase incident energy. And so I am under the impression residential services that are single phase 240 are under 1.2 cal anyway and therefore category 1 PPE is not necessary (ofcourse insulated gloves and eye protection still should be worn).
So I’m interpreting this article as even in residential single phase 240v i need to be wearing minimum 4 Cal arc rated long sleeve shirt, pants, arc rated face shield, arc rated jacket, hardhat, safety glasses, hearing protection, if im working on live panel board (sub panel and or main) with 240 V and below or get an incident energy analysis for every house im taking the cover off of the main service panel and testing voltages.
I feel like I’m not understanding correctly.
Which states
“ panel boards, or other equipment rated 240 V and below
Parameters maximum of 25KA available fault current; maximum of 0.03 seconds (2cycles) fault clearing time; minimum working distance, 455 mm (18”)
Arc flash PPE category one”
What I’m failing to find is any information regarding single phase and am interpreting this as, since I don’t know how to calculate the available fault current I’m supposed to get an incident energy analysis, but as far as I know, there is no calculation for single phase incident energy. And so I am under the impression residential services that are single phase 240 are under 1.2 cal anyway and therefore category 1 PPE is not necessary (ofcourse insulated gloves and eye protection still should be worn).
So I’m interpreting this article as even in residential single phase 240v i need to be wearing minimum 4 Cal arc rated long sleeve shirt, pants, arc rated face shield, arc rated jacket, hardhat, safety glasses, hearing protection, if im working on live panel board (sub panel and or main) with 240 V and below or get an incident energy analysis for every house im taking the cover off of the main service panel and testing voltages.
I feel like I’m not understanding correctly.