The 70E edition that's currently issued is 2024.
No, the labelling requirements have not changed.
Here's what that section says (from Link):
(H) Equipment Labeling.
Electrical equipment such as switchboards, panelboards, industrial control panels, meter socket enclosures, and motor control centers that are in other than dwelling units and that are likely to require examination, adjustment, servicing, or maintenance while energized shall be marked with a label containing all the following information:
- (1) Nominal system voltage
- (2) Arc flash boundary
- (3) At least one of the following:
- a. Available incident energy and the corresponding working distance, or the arc flash PPE category in Table 130.7(C)(15)(a) or Table 130.7(C)(15)(b) for the equipment, but not both
- b. Minimum arc rating of clothing
- c. Site-specific level of PPE
Exception No. 1:
Unless changes in electrical distribution system(s) render the label inaccurate, labels applied prior to the effective date of this edition of the standard shall be acceptable if they complied with the requirements for equipment labeling in the standard in effect at the time the labels were applied.
Exception No. 2:
In supervised industrial installations where conditions of maintenance and engineering supervision ensure that only qualified persons monitor and service the system, the information required in
130.5(H)(1) through
130.5(H)(3) shall be permitted to be documented in a manner that is readily available to persons likely to perform examination, servicing, maintenance, and operation of the equipment while energized.
-----------------------------------------------------------------------------------------------------------------------------------------------------------------
Some clients use "RED DANGER" for labels above 40 calories, and I think that's related to item 3(c) above, where it's considered site-specific labelling.