Wingrider
Member
- Location
- Northern Virginia
We have a few data centers for which I am the main consultant. The main question about arc flash mitigation pertains to, 'When is an arc flash study required on an existing building?' 'What mitigation must be applied to low (480 volt) and medium (12.47 kV) voltage switchgear?' We have several rackable circuit breakers that exceed the 40 cal/cm^2 incident energy level. Contacting the manufacturer, GE in this case, we were presented with three options; Remote Racking Operator (RRO), Entelliguard trip units, and an ArcVault. The RRO is about a tenth of the price of the other two solutions. The Entelliguard unit requires the operator to make a coordination change from Operations to Maintenance mode, which removes the time delay. The ArcVault is a passive device that extinguishes the arc in a remote vault. Will the RRO meet the letter of the law?