Hello All,
I was curious about NFPA 70E Article 130.5 (D) Equipment Labeling. The article states "Electrical equipment such as switchboards, panelboards, industrial control panels, meter socket enclosures, and motor control centers that are in other than dwelling units and that are likely to require examination, adjustment, servicing, or maintenance while energized shall be field-marked with a label." My question is if you did not account for every "control panel" on the project that was not within your purchase order or clearly labeled on your "scope" of work at the beginning of the project have you violated this code statement? Often times I will have a power systems study where no control panel or remote VFD is shown on the construction drawings for specific mechanical equipment, but may be provided by the mechanical contractor or manufacturer separately from the electrical install. Am I required to put a label on this equipment even if I was not aware of it or didn't define it in the scope of my equipment evaluation on my study. I would think that if a contractor had an energized work permit to work on equipment live and the equipment (maybe a control panel or remote VFD) did not have a label on it they would not touch it until further consultation. Thank you again for your help.
Best Regards,
Engineer in Training
I was curious about NFPA 70E Article 130.5 (D) Equipment Labeling. The article states "Electrical equipment such as switchboards, panelboards, industrial control panels, meter socket enclosures, and motor control centers that are in other than dwelling units and that are likely to require examination, adjustment, servicing, or maintenance while energized shall be field-marked with a label." My question is if you did not account for every "control panel" on the project that was not within your purchase order or clearly labeled on your "scope" of work at the beginning of the project have you violated this code statement? Often times I will have a power systems study where no control panel or remote VFD is shown on the construction drawings for specific mechanical equipment, but may be provided by the mechanical contractor or manufacturer separately from the electrical install. Am I required to put a label on this equipment even if I was not aware of it or didn't define it in the scope of my equipment evaluation on my study. I would think that if a contractor had an energized work permit to work on equipment live and the equipment (maybe a control panel or remote VFD) did not have a label on it they would not touch it until further consultation. Thank you again for your help.
Best Regards,
Engineer in Training