Could you elaborate on that? I dont have a 2017 yet...
(B) Service Equipment. In other than dwelling units, in addition to the requirements in (A), a permanent label shall be field or factory applied to service equipment rated 1200 amps or more. The label shall meet the requirements of 110.21(B) and contain the following information:
(1) Nominal system voltage
(2) Available fault current at the service overcurrent protective devices
(3) The clearing time of service overcurrent protective devices based on the available fault current at the service equipment
(4) The date the label was applied
Exception: Service equipment labeling shall not be required if an arc flash label is applied in accordance with acceptable industry practice.
Informational Note No. 1: NFPA 70E-2015, Standard for Electrical Safety in the Workplace, provides guidance, such as determining severity of potential exposure, planning safe work practices, arc flash labeling, and selecting personal protective equipment.
Informational Note No. 2: ANSI Z535.4-2011, Product Safety Signs and Labels, provides guidelines for the design of safety signs and labels for application to products.
Informational Note No. 3: Acceptable industry practices for equipment labeling are described in NFPA 70E-2015 Standard for Electrical Safety in the Workplace. This standard provides specific criteria for developing arc-flash labels for equipment that provides nominal system voltage, incident energy levels, arc-flash boundaries, minimum required levels of personal protective equipment, and so forth.