I appreciate the quick reply.
First, I would like to see where in 70E it states that I have to use an Arc Flash Label over the Hazard/Risk Category table.
Section 130.3 (B) states the following: One of the following methods shall be used for the selection of PPE:
(1) Incident Energy Analysis.
(2) Hazard/Risk Categories. The requirements of 130.7(C)(9),130.7(C)(10), and 130.7(C)(11)
As an electrician or operator, I interpret this like I have two options if the Label is on the equipment. I will go with option (2) if all I'm doing is operating a breaker open or closed with all doors and panels closed. Now if the breaker tripped or if there is reason to suspect a fault then I will go by the Arc Flash Label and suit up accordingly. We'll go with properly maintained and tested breakers and equipment for this situation.
Anyone see a problem with my rational or agree with me on this?