Hi All,
I have a question for the ARC Flash Study labels . I am a Project Engineer for a 10MW DC job which employs a DAS Monitoring system. The proposed system includes several Weather sensors and DAS Enclosure which requires 120V Input .
That said , per the NEC code 110.16 - "Electrical equipment, such as switchboards, switchgear, panelboards, industrial control panels, meter socket enclosures, and motor control centers, that is in other than dwelling units, and is likely to require examination, adjustment, servicing, or maintenance while energized, shall be field or factory marked to warn qualified persons of potential electric "arc flash hazards.
My understanding is this Enclosure would typically need an ARC Flash label . But , I do have a contractor who resists this installation as they think it is not needed given the voltage of 120V which is very less .
Any assistance of yours is very helpful. Thank you !
I have a question for the ARC Flash Study labels . I am a Project Engineer for a 10MW DC job which employs a DAS Monitoring system. The proposed system includes several Weather sensors and DAS Enclosure which requires 120V Input .
That said , per the NEC code 110.16 - "Electrical equipment, such as switchboards, switchgear, panelboards, industrial control panels, meter socket enclosures, and motor control centers, that is in other than dwelling units, and is likely to require examination, adjustment, servicing, or maintenance while energized, shall be field or factory marked to warn qualified persons of potential electric "arc flash hazards.
My understanding is this Enclosure would typically need an ARC Flash label . But , I do have a contractor who resists this installation as they think it is not needed given the voltage of 120V which is very less .
Any assistance of yours is very helpful. Thank you !