jimbo123

Senior Member
Can someone answer some question on arc flash labels on 480 v switchgear that is feed on both sides with a main breaker in service one at a time. label on main 1 says equipt: swgr-bus1 and the ocpd: is the utility - fuse. the other main says ocpd is gen. cb 1 Why the difference between both breakers ? Both mains have their own 3 transformers fed from same pole.
The feeder breakers are also labeled for the ocpd - gen. cb1

There are other equipment in plant fed from the feeders with labels that are labeled, equip : Mcc2 and the ocpd: swgr- fuse10. I am not sure how they got that.

Thanks for any help.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
I would recommend taking a look at the one-line diagram; venture to guess someone has made a labeling error, or not being consistent with naming convention.
 

wbdvt

Senior Member
Location
Rutland, VT, USA
Occupation
Electrical Engineer, PE
Check your one line and you may find that the second breaker is fed from a generator. The description you provided, gen. cb 1, seems like a generator plus why have 2 breakers from the same source on the same MCC?

There should have been a one line provided with the arc flash study that may provide your answer.
 