We have completed an arc flash coordination study, so I have the incident ratings for all of the breakers and switches. Now if the incident rating for a circuit breaker is 33 cal/cm, do I need to protect myself with a 40 cal suit to simply push the open or closed button on the breaker for commissioning testing? Does the arc flash incident rating only apply to open gear and exposed bus?
As previously stated, the 33 cal listing is the hazard. Any interaction entails a risk factor that theoretically could be lessened by plodding through ANNEX F of 70E, Hazard Analysis, Risk Estimation, and Risk Evalaution Procedure.
It's very typical to equate the HRC to the calcualted incident energy level, but the 70E 2012 edition puts that risk assessment on the owner, I think as a way to handle/lessen the sometimes overly stringent requirements.
But in support of this reduced risk associated with just operating the breaker from the front of the gear, Schneider Electric has their Data Bulletin 0100DB0804R11/09, PPE Recommendations Low and MV Equipment Operation/Maintenance. (wouldn't attach.. google it!)
This document lists four different classes of Square D equipment that can be operated from the front of the gear with PPE 0. It qualifies the installation as needing to: Have been commissioned; properly installed, rated and maintained; in operation under load....
But this gives an example of a manufacturer applying the "risk' factor to their gear and determining that the gear is safe to operate, unlike the impression that is given when you stick a PPE Dangerous tag on it. I haven't seen anything similar from other manufacturers.
So if your gear is this Square D class of gear, you could use this information; although the commissioning is not complete until you're finished and it's in operation!
You're probably stuck using remote operators, or the PPE 4 suit
John M