I've concluded from months of working on this topic, that the appropriate interpretation of Arc Flash PPE requirements around energized equipment is that the same PPE is required whether equipment covers are on or off.
The Arc Flash Boundary is a diameter around the equipment developed using the IEEE 1584 Arc-Flash Hazards calculations. (not using 70E tables - I'm using the calcs)
Given this interpretation, how can this practice be enforced? Is it being enforced in the field?
Using the example where there's a Power Distribution Unit (PDU) in a given floorspace. This PDU has a 300 kVA 480:208V transformer. The calculated incident energy at the secondary of the transformer is 40.1 cal/sq cm, necessitating a Dangerous Hazard Risk Category (HRC) - no safe PPE exists to approach the PDU in a 13 foot Arc Flash Boundary (AFB). (no main sec'y breaker on the PDU xfmr)
The "letter of the law" states that this equipment can't be approached while energized within that 13 foot boundary. Is anyone actually practicing this level of caution in the real world?
I want to issue Arc Flash labels, but I'm reluctant to advise a client that per NFPA 70E, they must stay out of the AFB around the equipment. The equipment is safe from Shock Protection with covers on, but it could explode from Arc Flash based on my calcs. Real world says the chances are very low that an Arc will develop, but since I've calculated the Incident Energy, I can't go back to the 70E tables for a relaxed PPE requirement.
What is a real-world approach to this situation?? Spray insulatory material on all busses and terminals to minimize the chance of an Arc?? But then how would that be tested...
Thanks for any comments.
John M
The Arc Flash Boundary is a diameter around the equipment developed using the IEEE 1584 Arc-Flash Hazards calculations. (not using 70E tables - I'm using the calcs)
Given this interpretation, how can this practice be enforced? Is it being enforced in the field?
Using the example where there's a Power Distribution Unit (PDU) in a given floorspace. This PDU has a 300 kVA 480:208V transformer. The calculated incident energy at the secondary of the transformer is 40.1 cal/sq cm, necessitating a Dangerous Hazard Risk Category (HRC) - no safe PPE exists to approach the PDU in a 13 foot Arc Flash Boundary (AFB). (no main sec'y breaker on the PDU xfmr)
The "letter of the law" states that this equipment can't be approached while energized within that 13 foot boundary. Is anyone actually practicing this level of caution in the real world?
I want to issue Arc Flash labels, but I'm reluctant to advise a client that per NFPA 70E, they must stay out of the AFB around the equipment. The equipment is safe from Shock Protection with covers on, but it could explode from Arc Flash based on my calcs. Real world says the chances are very low that an Arc will develop, but since I've calculated the Incident Energy, I can't go back to the 70E tables for a relaxed PPE requirement.
What is a real-world approach to this situation?? Spray insulatory material on all busses and terminals to minimize the chance of an Arc?? But then how would that be tested...
Thanks for any comments.