Which value is correct current in determining upstream OCPD clearing time ?
Simple 2 point system
Panel A has an OCPD that serves panel B.
bf = boltedfault af = arcing fault
Panel A : Ibf= 44,940.01 amps
Feeder to Panel B>>> 100’ - 1 set - #3's - Single conductors - Steel conduit
Panel B : Ibf= 10,221.30 amps, calc >>>> Iaf = 6,681.32 amps
REFLECT Iaf = 6,681.32 amps back to Panel A , calc>>>> Isc = 13,497.47 amps
Utilize Isc = 13,497.47 amps to derive CLEARING TIMEat OCPD at Panel A.
Agree or disagree ??