big john
Senior Member
- Location
- Portland, ME
Is a hardhat a PPE requirement for all arc-flash protection above Category 2?
I found a supplier selling an arc-flash face-shield that can be worn without a hardhat. The shield is rated for 12cal/cm2 which puts it above the minimum Category 2 protection rating. It also provides chin and forehead protection.
But from the looks of it NFPA 70E 130.7(C)(10) requires a hardhat for anything over Category 1... no exceptions? Is this correct? How is this face shield compliant?
(As an aside, I'd like to get it just because this stuff is so darn hot... the less of it that has to be worn, the easier it is to work in.)
-John
I found a supplier selling an arc-flash face-shield that can be worn without a hardhat. The shield is rated for 12cal/cm2 which puts it above the minimum Category 2 protection rating. It also provides chin and forehead protection.
But from the looks of it NFPA 70E 130.7(C)(10) requires a hardhat for anything over Category 1... no exceptions? Is this correct? How is this face shield compliant?
(As an aside, I'd like to get it just because this stuff is so darn hot... the less of it that has to be worn, the easier it is to work in.)
-John