timm333
Senior Member
- Location
- Minneapolis, MN
- Occupation
- Electrical Design Engineer
NEC-2014 section 240.87(B)(3) requires an arc flash reduction switch for breakers 1200A or higher. This means that when the main breaker of a local panel is 1200A or higher, we put an arc flash maintenance switch for maintenance.
What if the distribution panel does not have main breaker, and the main breaker is located in the upstream switchgear; in this case shall the arc flash maintenance switch be required in the local panel or in the upstream switchgear? Thanks
What if the distribution panel does not have main breaker, and the main breaker is located in the upstream switchgear; in this case shall the arc flash maintenance switch be required in the local panel or in the upstream switchgear? Thanks