How does everyone treat motor loads when doing arc flash studies? Obviously, in most cases, you can never be sure which motors will be running if an arc flash were to occur.
I normally ignore smaller motors, but for groups of motors that add up to a significant HP (like on MCC's), I'll add the motors horsepowers together, and assume some fraction is running.
And for large motors, I'll add them into the study individually.
Then I'll usually try different combinations of motors on and off, and try to get an idea of what the worst case is going to be. (If a building has a lot of motors, you obviously can't try every single combination of on and off).
The reason I ask is that I recently saw an arc flash study for a building and it didn't include any loads what so ever. No motors or any other loads of any kind. At a minimum, I'm sure this building has some larger HVAC units. Its not a huge building, but it has (2) 1500 KVA transformers that supply it.
I normally ignore smaller motors, but for groups of motors that add up to a significant HP (like on MCC's), I'll add the motors horsepowers together, and assume some fraction is running.
And for large motors, I'll add them into the study individually.
Then I'll usually try different combinations of motors on and off, and try to get an idea of what the worst case is going to be. (If a building has a lot of motors, you obviously can't try every single combination of on and off).
The reason I ask is that I recently saw an arc flash study for a building and it didn't include any loads what so ever. No motors or any other loads of any kind. At a minimum, I'm sure this building has some larger HVAC units. Its not a huge building, but it has (2) 1500 KVA transformers that supply it.