PSU Electrical
Member
- Location
- Bethlehem/Scranton
We just recently finished a new addition to an industrial plant. All of the power distribution equipment for the addition was taken all the way back to the primary substation for the plant. So we have a 4kV feed from the primary substation switchgear lineup to a new 4160/480VAC Unit Substation and a few MCC and Panelboards beyond that. The client requested whether we can get an Arc Flash Study (and Short Circuit and Protective Device) done for the new addition. I would like to meet this request but all of the studies I have done were for the entire facility whereas in this situation, I'm only doing a portion of the overall power system. Can I do the Arc Flash, SC and PD Study for this new addition (and do it accuratly of course) by only modeling the new equipment back to the primary service switchgear or do I truly need to model the rest of the plant? I understand the plant could have motor contribution and such but if I simply took the remaining plant load and total motor contribution, can I just put that in as a lumped load? What, if any, would be the difference in Arc Flash and SC levels if I DO and I DON'T model the rest of the plant? Any feedback would be appreciated.
Chris (ETAP user)
Chris (ETAP user)