I have some questions/comments about arc flash studies based on my recent experience with one.
- What are transformers considered as far as equipment type based on IEEE 1584 2018? Does it even matter what the type is as long as internal dimensions, conductor gap, and working distance are accurate? I can’t purchase the 2018 standard at the moment so I’m relying on online calculators. My thought is that it would be type MCC/Panel – Deep.
- For panelboards with MCBs, which OCPD do you use for clearing time? If the fault is upstream of the MCB, which I would think would occur most of the time, then the upstream OCPD should be used, however faults can occur on the bus in which case the MCB would be more relevant. My thought is that faults occurring upstream of the MCB will always result in longer or equivalent clearing times, and hence higher incident energy, so the upstream OCPD should always be used.
- If an arc fault occurs before the first feeder OCPD from the service transformer, what stops the arc? Surely it will not cause any utility-side fuse to blow, so does it just persist until enough of the infrastructure has blown apart and burned away?
- In almost every case here working with 480 VAC supply voltage and about 10 kA available fault current from the utility, the incident energy has been calculated at less than 1.2 cal/cm^2. The two exceptions are counter-intuitive: 208 VAC distribution panels downstream from 480/208 transformers. These resulted in 7-8 cal/cm^2 due to the maximum OCPD clearing time of 2 seconds. I understand the reasons why this is, but it’s amazing that these panels wouldn’t have even been considered in IEEE 1584 2002. It also tells me that as a design consideration, OCPD should be provided closer to the transformer secondary and outside of the distribution panel to prevent these types of panels from having ridiculous ratings.
- How does the POCO determine the available fault current at the service transformer secondary? Do they actually calculate line impedance all the way back to the power plant alternators? There has been significant development around here and I know for a fact utility lines have been upgraded, however the POCO did not change their estimate from three years ago to this year.