All of my Arc Flash Incident Energies are between 12-21 Cal/Cm2.
I will be recommending tech's wear a 25 Cal suit on the Arc Flash label.
NFPA 70E is silent if the Techs wear a long sleeve shirt and pants under the 25 Cal suit.
I have seen both ways done. Any 2 cents? Don't want to overheat the techs, but any
supplement protection is worth it.