Difficult to answer question.
I'm a Consulting Engineer. Virtually 99% of the time, POCO's won't give REAL available fault currents. The numbers they give us "surprisingly" work out to nothing more than the xfmr Z with infinite primary bus reflected to the secondary (our SE). OK, they want to cover their butts so that we adequately provide interrupting gear that exceeds the worst-case. However, a very different (dangerous) thing happens when you do an Arc Flash Study. It is totally counter-intuitive, but often a higher supply fault current will CLEAR faster than a much-smaller service. The opposite is that a lower fault current will often result in a HIGHER hazard than a larger fault current because it will burn-longer (take longer to clear). The formula's are only as good as what data they are provided. However, when we base ALL our computations and ALL our labeling on an unrealistically (but unverifiable) figure from a utility EVERYTHING we calculate and label will ultimately be wrong. The result is that a higher hazard may actually exist because the utility gave us an unrealistically large fault current. After all it NEVER is actually an infinite primary bus.
How do others reconcile this conundrum when calculating Arc-Flash data and labeling?
I'm a Consulting Engineer. Virtually 99% of the time, POCO's won't give REAL available fault currents. The numbers they give us "surprisingly" work out to nothing more than the xfmr Z with infinite primary bus reflected to the secondary (our SE). OK, they want to cover their butts so that we adequately provide interrupting gear that exceeds the worst-case. However, a very different (dangerous) thing happens when you do an Arc Flash Study. It is totally counter-intuitive, but often a higher supply fault current will CLEAR faster than a much-smaller service. The opposite is that a lower fault current will often result in a HIGHER hazard than a larger fault current because it will burn-longer (take longer to clear). The formula's are only as good as what data they are provided. However, when we base ALL our computations and ALL our labeling on an unrealistically (but unverifiable) figure from a utility EVERYTHING we calculate and label will ultimately be wrong. The result is that a higher hazard may actually exist because the utility gave us an unrealistically large fault current. After all it NEVER is actually an infinite primary bus.
How do others reconcile this conundrum when calculating Arc-Flash data and labeling?