arc flash

Status
Not open for further replies.

highline

Member
Where are some of you drawing the line for placement of arc flash signs? If we were to place a label on every piece of equip. that gets worked on hot I'll be busy for awhile. Or did I miss something on what has to and does not have to have a warning? All info will be much apreciated.
 

bphgravity

Senior Member
Location
Florida
Re: arc flash

Signage, tagging, identifying, etc.. are some of the most neglected practices in our industry. As with most of the rest of the NEC, 110.16 provides a good starting point. Arc Flash warnings are not necessarily meant to provide information to a qualified person but act as a reminder of the dangers involved. It prevents us from becomming complacent in what we do and how we do it.
Stickers and signs cost cents and require no more than a few seconds to apply.
In the event of an accident, OSHA and the insurance company may be interested in why some equipment was deemed worthy of signage and why others were not. Just something to consider.
I was recently inside a building well over 100 years old that still contained some of the original wiring and switching equipment from the early 1930's. Above a huge open, uninsulated , and exposed switchboard was a sign that stated: "Danger, Energized Equipment May Explode Or Catch Fire." This message was hand written and appeared to be original to the installation. The equipment is no longer in use and right next to this vintage apparatus are the new panelboards servicing the building. These panels have no signage, no warnings, no indication at all of any danger. Obviously this equipment are completey enclosed and deadfronted, but the energy levels and available fault currents are much greater than the original circuits. It just seemed ironic.
 

rick5280

Senior Member
Re: arc flash

Since the code is not retroactive, for the most part, you are not required to sticker every panel or piece of equipment you see. Just put it on any new piece you install, and then only where required.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: arc flash

Originally posted by rick5280: Just put it on any new piece you install, and then only where required.
This is the part that confuses me. 110.16 just says that panels, etc. ?shall be field marked. . . .? It does not say by whom, nor when. It does not tell me that the label must be in place as part of the electrician?s task, and that it must be done prior to final inspection.

To the Inspectors who participate in the Forum: Do you see it as your job to verify the label is in place before you accept the installation?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: arc flash

In Washinton State, arc flash labels are not being required by our state AHJ's.
But I carry arc flash labels and install them when I do an installation.
 

ryan_618

Senior Member
Re: arc flash

To the Inspectors who participate in the Forum: Do you see it as your job to verify the label is in place before you accept the installation?
Yes. I ask for the sticker at the power to panel inspection. Typically they don;t have it in place. I allow the inspection to pass, but I require the sticker on the final inspection.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: arc flash

Why should this be done in the field? Why not by the manufacturer? The field marking requirement is left over from the original proposal that would have required the posting of the arc/blast/flash calculations on the panel. That would have to be done in the field, but when the requirement to provide the calculations was removed from the rule, the requirement for field marking should have also been removed.
Don
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Re: arc flash

Don,

This answer may seem a bit convoluted but please bear with me.

To say the NEC is not retroactive is not absolutely true. It is a matter of who is enforcing and what they are enforcing. There is a hint of this intent in 80.9 (B) - even if Art. 80 only applies where specifically adopted:

(B) Existing Installations. Existing electrical installations that do not comply with the provisions of this Code shall be permitted to be continued in use unless the authority having jurisdiction determines that the lack of conformity with this Code presents an imminent danger to occupants. Where changes are required for correction of hazards, a reasonable amount of time shall be given for compliance, depending on the degree of the hazard.
Both Fed and State OSHA organizations can (and often do) enforce consensus codes retroactively if they believe worker safety is involved. AS stated in the NEC handbook for 110.16:
This requirement is new in the 2002 Code. Field marking that warns electrical workers of potential electrical arc flash hazards is now required because significant numbers of electricians are being seriously burned or killed from accidental electrical arc flash while working equipment ?hot? (energized).
Since most existing panels are not currently marked for flash hazard, field marking is the only option for existing installations. Factory marking may of course be specified.

The 70E Tech Committee envisioned that before any work on energized equipment were started, field marking would be added as part of the safety analysis. And there is no ?grandfathering? out of a safety analysis. Also remember the 2000 70E, came out before the 2002 NEC. For all practical purposes 70E was constrained in Part I to use text taken from the latest NEC (1999) at the time. So what was envisioned was not completely documented.

[ May 18, 2004, 05:08 PM: Message edited by: rbalex ]
 

bphgravity

Senior Member
Location
Florida
Re: arc flash

This topic is like most things having good points on both sides.

It would certainly be alot easier and more pratical for manufacturers to provide an arc-flash hazard sticker with the equipment. It would be similar to GFCI manufacturers that provide the "GFCI protected" and "No Equipment Ground" stickers. I like the idea.

On the other hand, these stickers and signs should still be available for field use to augment the manufactrers signage or for use on existing equipment. :)
 

tepres

Member
Re: arc flash

I also agree that it would be nice if the labels were provided with (not applied to) the equipment.

My understanding is that Arc-flash hazards do not exist in every installation. This depends on voltage, available fault current, etc... Arc-fault calculations would need to be performed to determine if a hazard even exists. So, field marking would be the only accurate method.
Is there any harm in applying a label where a hazard does not exist? Probably developing complacency over time.

Further, IMO, once you start applying labels at your or someone elses facility, an effort should be made to apply them throughout. Even if it's accomplished over time. The hazards still exist on the existing equipment. Even more so in some cases. Seeing labels on some equipment and not on others may instill a false sense of security.

just my $.02
 