I'm an Electrical Engineer studying up on Arc Flash. It seems to me based on NFPE 70E that the PPE (Personal Protective Equipment like fire suits) requirements are only if someone has exposed live conductors. The Arc Flash boundary does not seem to exist if there are no exposed live conductors. (see definition of arch flash boundary in NFPE 70E)
To me this means that if someone deenergizes (lockout/tagout and grounds) a 480V MCC or switchgear, for example, then works on the equipment with no PPE. Later, they finish the work, close up the MCC, and are ready to close the main breaker on the MCC/switchgear. Do they need to have PPE to close that main breaker right in front of the MCC/switchgear?
I?m concerned with the literatures ambiguity/vagueness stating that they don?t, but safety says they do. I imagine a case where they close onto a fault in the MCC/switchgear. When they close the breaker effectively an explosion occurs in the panel and that flimsy cover isn?t going to help that guy from getting severe burns.
I think that none is necessary to be compliant with NFPA 70E but one should for safety anyway.
To me this means that if someone deenergizes (lockout/tagout and grounds) a 480V MCC or switchgear, for example, then works on the equipment with no PPE. Later, they finish the work, close up the MCC, and are ready to close the main breaker on the MCC/switchgear. Do they need to have PPE to close that main breaker right in front of the MCC/switchgear?
I?m concerned with the literatures ambiguity/vagueness stating that they don?t, but safety says they do. I imagine a case where they close onto a fault in the MCC/switchgear. When they close the breaker effectively an explosion occurs in the panel and that flimsy cover isn?t going to help that guy from getting severe burns.
I think that none is necessary to be compliant with NFPA 70E but one should for safety anyway.