zog said:
True, but it is in 2009 which is released. I promise that if you have a fatality from an arc flash labeled >40cal, OSHA will find a way to enforce it. General duty clause seems to be the "company" answer. But really, dont you think you should not work >40cal when you know it is unprotectable? Even if it was "technically" unenforceable? Could you sleep with that if something happened? I couldnt.
Still can't find it in the 2009... The closest I see is FPN No. 2 of 130.7(A):
"When incident energy exceeds 40cal/cm2 at the working distance, greater emphasis may be necessary with respect to de-energizing before working within..."
I'm not saying that you SHOULD work it, or allow it. I'm just saying that it's not in any code anywhere.
For a company to allow it does indeed expose them to additional unjustifiable liabilities, but legally there is no requirement. If I was working or advising a company that insisted on allowing work above 40 cal, I would at least advocate that they should inform their workers of the additional risks of such work.