j rae said:What are the rules for wearing arc flash safety equipment? I was told any time you remove a panel cover you are requried to ware saftey gear.
jim dungar said:You must always wear the appropriate PPE when working/interacting with or near energized parts. All parts must be consider energized until they have been verified as de-energized with a meter.
S'mise said:We are required to wear #2 fire rated clothing at a min. #5 for working on switchgear.
S'mise said:.
The added bonus to wearing proper ppe is looking like a beekeeper
augie47 said:plus sweating off pounds and pounds.
zog said:What is #5? Dosent exist, you must work at Ford, hey had alot of mislabeled HRC 5 switchgear, those should be relabeled as "Dangerous" and it must be worked on denergized and utilize remote switching and racking systems, or find a way to reduce the hazard.
WDeanN said:Under what standard? There is no blanket requirement in the NFPA 70E to de-energize above 40 cal. The misunderstood statement is in the handbook, which is unenforceable.
It may be a good practice, but it is not in the standards. As such it is up to the facility.
zog said:True, but it is in 2009 which is released. I promise that if you have a fatality from an arc flash labeled >40cal, OSHA will find a way to enforce it. General duty clause seems to be the "company" answer. But really, dont you think you should not work >40cal when you know it is unprotectable? Even if it was "technically" unenforceable? Could you sleep with that if something happened? I couldnt.
opb said:I am not questioning this but inquiring. You can get suits that are rated greater than 40 cal so what makes it unprotectable?
Thanks.