I don’t see in 210.12 where bathroom light are on a ARC breaker? Does anybody know where it say’s it in the code book?
Last edited:
It doesn't. It seems bathrooms and garages are the only areas left out and I don't consider either to be "similar areas"I don’t see in 210.12 where bathroom light are on a ARC breaker? Does anybody know where it say’s it in the code book?
They would only be required to be on an AFCI if the lights were also in other rooms on this same circuit that required AFCI.I don’t see in 210.12 where bathroom light are on a ARC breaker? Does anybody know where it say’s it in the code book?