Re: arc requirment

Greg,
I don't see a need for looking at another thread. If you are using the 2002 or 2005 code, it is very clear that the 110 volt smoke alarm in a dwelling unit bedroom must be served by a branch circuit that has AFCI protection.
Don
 
Re: arc requirment

Yes, Don I agree. I was just trying to help him out by reading the conversations re 210.12(B) 05' NEC.
 
Re: arc requirment

Jeff AFCI's were first required in the 1999 NEC and then the requirements expanded in the 2002.
Look for more AFCI requirements with future code editions.
The CMP clearly meant for the dwelling unit smoke detectors to be AFCI protected.
Three years ago we had so many AFCI quesitons, we had a separate topic for them. This is the first AFCI question I have seen in months.
 
Re: arc requirment

I work with a company that has forty lisenced electricians installing smokies on their own circuit, not arc-fault protected. We are under the 2005 code. The AHJ does not have a problem with this. We have been doing this for almost two years now.
 
Re: arc requirment

Originally posted by Jeff Rae:
is a 120 volt smoke detector in a bedroom need acr ckt. protection
Check your local codes. Here in Indiana, the requirement for arc fault protection was deleted from our state code.
 
Re: arc requirment

Originally posted by sparkslord:
I work with a company that has forty lisenced electricians installing smokies on their own circuit, not arc-fault protected. We are under the 2005 code. The AHJ does not have a problem with this. We have been doing this for almost two years now.
That doesn't make it right. NEC requires arc fault protection and some regulations require smokes to be fed from general purpose branch circuits. Your inspector is not doing his job and if you are willingly violating the code simply because the inpsector allows it you aren't doing yours either.
 