Okay, so I have one of Mike Holt’s video set. He said something that really got me wondering.
Let me set the scene.
In his 2017 video series on Understanding the Code (Art 502 in Hazardous location) he goes on this long winded talk about objectionable current. Objectionable current is an issue in hazardous locations because of arching and sparking. So, that’s why bonding bushings and bonding jumpers are required. It helps prevent possible issues with loose locknuts if there’s objectionable current. (Objectionable current comes about when the neutral and the equipment grounding conductor are tied together in a location other than the service or the secondary side of transformer)
Please help me sort out what you read below:
He said very casually that fault current is less of an issue with causing arching and sparking with loose locknuts. He said this was because of the amount of amperage at the time of the fault. Could be like 2000Amps.
But he said objectionable current was a bigger issue. A loose connection with less current is a bigger issue with arching.
What I gathered from this was that fault current would make a very strong connection back to the source regardless of the loose locknuts. Which would cause less of an arch and less spark. Whereas the objectionable current would be in normal current ranges (lets say 20 amps) and pose a bigger risk of igniting. I don’t really understand this. Any input on this topic would be greatly appreciated
Let me set the scene.
In his 2017 video series on Understanding the Code (Art 502 in Hazardous location) he goes on this long winded talk about objectionable current. Objectionable current is an issue in hazardous locations because of arching and sparking. So, that’s why bonding bushings and bonding jumpers are required. It helps prevent possible issues with loose locknuts if there’s objectionable current. (Objectionable current comes about when the neutral and the equipment grounding conductor are tied together in a location other than the service or the secondary side of transformer)
Please help me sort out what you read below:
He said very casually that fault current is less of an issue with causing arching and sparking with loose locknuts. He said this was because of the amount of amperage at the time of the fault. Could be like 2000Amps.
But he said objectionable current was a bigger issue. A loose connection with less current is a bigger issue with arching.
What I gathered from this was that fault current would make a very strong connection back to the source regardless of the loose locknuts. Which would cause less of an arch and less spark. Whereas the objectionable current would be in normal current ranges (lets say 20 amps) and pose a bigger risk of igniting. I don’t really understand this. Any input on this topic would be greatly appreciated