RiseFromYourGrav
Member
- Location
- Chicago, Il
I work for a small switchboard builder, and we are working on a 2000A 208V 100kAIC switchboard that the customer requested to have a fused bolted pressure switch for a main. We figured there would be a fuse out there that would keep us compliant with NEC 240.67, but the arcing energy at that level of fault current is not very high, so it's hard to find a fuse that could clear that in 0.07 seconds (and the fault current is very likely a lot lower than 100kA). My question is: within a multi-section low voltage switchboard, can we just say it is a VCBB configuration if we barrier the line/load lugs, or does the rest of the bus being not barriered require us to go to VCB? There's a fuse we can use that clears 18kA in 0.07 seconds, and the VCBB configuration would take us to 19kA based off of the easy Bussmann calculator (32mm gap, 100kA fault current). If there is another equation that might suit us better knowing the exact size of the switchboard and whatnot, that would help. We would then have to go back to our customer for more information to get the real fault current and see if the fuse would still work. In the future, we're going to all breakers at this voltage/ampacity combo...