430.22(A) Single Motor - conductors that supply a single motor used in a continuous duty application shall have an ampacity of not less than 125% of motor's FLA.
215.2(A)(1) - feeder conductors shall have an ampacity not less than 100% of non-continuous load plus 125% of the continuous load.
Question: do these two mean the same thing or are these two adjustments applied separately?
Example: 100A motor rated continuous-duty
a) Assuming motor will never be used more than 2hr59min at a time, 100 x 1.25 = 125A (per 430.22(A))
b) Assuming motor will run > 3 hours at a time, 100 x 1.25 x 1.25 = 156.25A (per 430.22(A) AND 215.2(A)(1))
Are both "a" and "b" correct interpretations of these two sections of the NEC?