A slash rated breaker restriction is due to the L-G insulation in the construction of the breaker and not its AIC rating.It depends on what the voltage rating is listed as on the breaker. For instance, if a breaker is rated 480/277, the AIC is based on the L-N voltage, so it CANNOT be used on a Delta system. If a breaker just lists a voltage by itself, it is rated at the L-L voltage; so a breaker rated 600V, the AIC is based on whatever the line-to-Line voltage is that you are using.
D'oh! I know that. The slash rating issue has been coming up a lot for me lately and I find myself having to explain it to people who were completely unaware that it even existed. I jumped the gun a bit here. Mea culpa.A slash rated breaker restriction is due to the L-G insulation in the construction of the breaker and not its AIC rating.
A three pole 480Y/277 breaker recieved its AIC level after being tested with a 3-phase L-L bolted fault. A single pole breaker can only have a L-N AIC rating. The published AIC of a multi-pole breaker is always a L-L rating (in fact, its L-N AIC level may be lower).
All I can say is, I need to stop posting late at night...