Are B-Hubs Bonding?

Simpuller

Member
Location
MO
Occupation
Engineer
Is a BHub bonding?
I have a Nema 3R breaker enclosure that's going to be my primary disconnect.
It's a Q23225NRB, RB suffix for B-Hub connection of my service mast.
Cut sheets are attached.
It seems that as this panel is suitable for service entrance equipment and its expected connection is BHub, that BHubs would be bonding.
The top entry is sized for max 2-1/2 in, so what would anybody do for bonding hub sizes other than 2-1/2 in.
Any thoughts?
 

Attachments

  • Schneider Electric_QO-Load-Centers_B250.pdf
    426.3 KB · Views: 22
  • Service Panel Q23225NRB 3288.pdf
    76.8 KB · Views: 14
I say yes. When I nipple a W/P panel under a meter, the nipple is considered bonded by the OEM bolt-on hub.
 
Thanks folks. I thought so, but couldn't find it in the cut sheets.
You'd think they would say it's bonding any chance they got.
 