Do short sections of raceways such as EMT stubbed thru floors require adapters and bushings to protect the NM Cable or is it permissible to simply ream the EMT? :-?
Do short sections of raceways such as EMT stubbed thru floors require adapters and bushings to protect the NM Cable or is it permissible to simply ream the EMT? :-?
You need a bushing to change from EMT to NM. The code used to read, "fitting". It didn't say what kind. But now you actually have to have the right fitting
I think this makes good sense. Will you please provide the code section? Thank you in advance.![]()
Working off memory,,,,334.15,,,,b,,, i think calls for EMT
314.42 calls for bushing
I think there's another in there somewhere
300.15 (C) Protection. A box or conduit body shall not be required where cables enter or exit from conduit or tubing that is used to provide cable support or protection against physical damage. A fitting shall be provided on the end(s) of the conduit or tubing to protect the cable from abrasion.
raco makes a changeover from emt to a rx connector