Should a breaker be replaced after it has succesfully opened two short circuits if the current was at the maximum breaker short circuit rating
IEEE Std 1015-1997 - Blue Book
3.35 circuit breaker useful Life - It is prudent to replace any MCCB that has interrupted , at most, two faults at rated maximum current
IEEE Std 902-1998 - Yellow Book
Protective Device Testing
6.3.2 Low-Voltage Circuit Breakers
Covers Power Circuit Breakers, Molded Case Circuit Breakers and Insulated Case Circuit Breakers
Power circuit breaker have mechanical adjustments and inspections that should be periodically checked.
Tests should confirm devices perform within time-current specifications provided by manufacturer and are calibrated to conform to the coordination study.
NEMA AB 4-1996 For Molded Case Circuit Breakers
Recommended Tests
Visual Inspection for overheating
Mechanical Operation
Insulation Resistance Test
Individual Pole Resistance Test
Inverse Time Overcurrent Trip Test
Instantaneous Overcurrent Trip Test
Rated Hold-In
Just my $.02