OK I will answer the question that was not asked.
For a dwelling unit, receptacles are required on 12 ft spacing, and the load for those receptacles is included in the 3 watts/sq ft, and you can have 100 15 ampere receptacles on a circuit.
For a non-dwelling unit (commerical is not a NEC term) no receptacles are required in office areas but if you include them they count at 180 VA each.
So in a non-dwelling occupancy, when you install a 15 or 20 amp, 125 volt receptacle, its included in the load calculation and those rules take an entire artice - 220.
What typically happens is we apply the dwelling unit receptacle rules to non dwelling units. Same with light switches, an office area does not require a light switch.